Whale heating
We're having problems with our heating not working on gas or electric. Comes on then we have a red light flashing and it stops working. Any suggestions please.
judy- Member
-
Posts : 152
Joined : 2014-08-19
Member Age : 74
Location : Lochaber
Auto-Sleeper Model : kemerton
Vehicle Year : 2015
Re: Whale heating
Judy
I would make a measured guess that the red light flashing indicates overheating. The first thing to check is that the air inlet and outlet are both clear of any obstruction.
Keith
I would make a measured guess that the red light flashing indicates overheating. The first thing to check is that the air inlet and outlet are both clear of any obstruction.
Keith
KMRTOPAZ- Donator
-
Posts : 868
Joined : 2014-12-26
Member Age : 91
Location : Sandbach Cheshire
Auto-Sleeper Model : Topaz T5
Vehicle Year : 2013
Re: Whale heating
Hi Judy , does the fan start before the red light comes on . If the fan does not start then the unit will not start to heat either on gas or electric as there is no air flow to remove heat from the elements .Try google I think you count the number of flashes which indicates the specific problem
kaspian- Member
-
Posts : 1372
Joined : 2015-09-27
Member Age : 64
Location : ayrshire - Burns country
Auto-Sleeper Model : WARWICK XL
Vehicle Year : 2017
Re: Whale heating
Thanks folks. Yes we've tried vents. Not sure if it could have been overheating. We'll try it again tomorrow when we have time. It's such a trail to go back to Perth again (as well as the expense out of our pockets !). We had just got it back from being repaired . Drove home 100 miles, and parked it for the night . Packed up a few days later , went to a beautiful beach site with no hook up and that's when it worked for an hour then wouldn't. Next site had hook up. Again it appeared to work but after a few minutes the red light was flashing so no I don't think it was overheating causing the problem. I'll phone them again and see what they come up with.
judy- Member
-
Posts : 152
Joined : 2014-08-19
Member Age : 74
Location : Lochaber
Auto-Sleeper Model : kemerton
Vehicle Year : 2015
Re: Whale heating
As said, I believe the 'pattern' of the flashes give a clue to the problem and that's detailed in the Whale documentation. Whale also provide superb direct customer serice, so rather than incur time and cost of returning to the dealer, I'd give them a ring if their handbook doesn't help.
steamdrivenandy- Member
-
Posts : 1842
Joined : 2016-03-30
Member Age : 76
Location : On the very edge of N Staffs
Auto-Sleeper Model : None
Vehicle Year : None
Re: Whale heating
Worth checking the temp sensor controlling the heat in the van. We had a similar problem, flashing red light etc, no heat, nothing. Found that the sensor cable had become detached from the sensor. Reconnected, perfect. Must say we are talking about a Sussex Duo, but same principle I guess.
Tengah74- Member
-
Posts : 223
Joined : 2013-02-23
Member Age : 83
Location : Luton
Auto-Sleeper Model : Sussex duo
Re: Whale heating
Hi Judy,
Should it be the same model as mine you can download the instructions from whale.
this is from the book.
the numbers refer to the number of flashes and what they mean also to override a lockout, you just have to switch it off and on again within two and a half seconds.
1 No flame detected Check gas supply.
2 Overheat Check the air ducts and vents are not blocked or restricted. We recommend you wait at least 5 to 10 minutes to allow the heater to cool before clearing lockout.
3 Low/High Supply Voltage Ensure voltage is above 10V at the heater and below 15V.
4 Combustion Air Fault Check combustion air flue and exhaust flue for
blockages.
5 Other / internal fault Attempt to clear lockout as shown below. If this fails contact Whale Heating Support: 0845 217 2933.
To clear any lockout switch off and back on within 2.5 seconds
Space Heater Fault Finding
Should it be the same model as mine you can download the instructions from whale.
this is from the book.
the numbers refer to the number of flashes and what they mean also to override a lockout, you just have to switch it off and on again within two and a half seconds.
1 No flame detected Check gas supply.
2 Overheat Check the air ducts and vents are not blocked or restricted. We recommend you wait at least 5 to 10 minutes to allow the heater to cool before clearing lockout.
3 Low/High Supply Voltage Ensure voltage is above 10V at the heater and below 15V.
4 Combustion Air Fault Check combustion air flue and exhaust flue for
blockages.
5 Other / internal fault Attempt to clear lockout as shown below. If this fails contact Whale Heating Support: 0845 217 2933.
To clear any lockout switch off and back on within 2.5 seconds
Space Heater Fault Finding
breakaleg- Member
-
Posts : 1163
Joined : 2011-06-01
Member Age : 68
Location : Birmingham
Auto-Sleeper Model : Nuevo Ek
Vehicle Year : 2021
Re: Whale heating
Thanks everyone for all the suggestions. Did everything we possibly could then decided to follow Steamdrivenandy's suggestion to phone whale direct. Spoke with A very helpful lady and the result is that an engineer is calling to our house to fit a new space heater !! How's that for service. He's coming on Sunday ! So thanks again everyone. Sorry I have taken so long in replying.
judy- Member
-
Posts : 152
Joined : 2014-08-19
Member Age : 74
Location : Lochaber
Auto-Sleeper Model : kemerton
Vehicle Year : 2015
Similar topics
» Whale heating cutting out
» Whale duo heating not working on gas
» Whale heating temperatures
» Whale heating faults
» Warwick Duo - new van - Whale Heating System
» Whale duo heating not working on gas
» Whale heating temperatures
» Whale heating faults
» Warwick Duo - new van - Whale Heating System
The Auto-Sleeper Motorhome Owners Forum (ASOF) :: Auto-Sleeper Motorhome Forums :: Auto-Sleeper "Van Conversions" Forum
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum